1. A branch circuit supplies 16 A of continuous load and nothing else. What is the minimum overcurrent device rating?
- A.15 A
- B.20 A
- C.16 A
- D.25 A
Answer: B. Continuous loads are sized at 125 percent: 16 x 1.25 = 20 A, and 20 A is a standard rating. A 15 A or 16 A device would be loaded past 80 percent continuously.
2. What is the largest single cord-and-plug load permitted on a 20 A receptacle?
- A.12 A
- B.15 A
- C.20 A
- D.16 A
Answer: D. A cord-and-plug-connected load on a 20 A receptacle may not exceed 80 percent of the receptacle rating, which is 16 A.
3. A kitchen countertop wall space must have a receptacle when it is at least this wide:
- A.12 in.
- B.24 in.
- C.6 in.
- D.18 in.
Answer: A. Every countertop and work surface wall space 12 in. or wider gets a receptacle outlet. Spaces narrower than that do not need one.
4. Which receptacle ratings are permitted on a 20 A general-purpose circuit with two or more receptacles?
- A.15 A only
- B.20 A or 30 A
- C.15 A or 20 A
- D.20 A only
Answer: C. On a multi-outlet 20 A circuit, receptacles rated 15 A or 20 A are allowed. A 30 A receptacle belongs on a 30 A circuit.
5. What is the minimum number of small-appliance branch circuits for a dwelling kitchen and dining area?
- A.Two 15 A circuits
- B.Three 20 A circuits
- C.Two 20 A circuits
- D.One 20 A circuit
Answer: C. At least two 20 A small-appliance branch circuits are required, and the countertop receptacles must be served by at least two of them.
6. The branch circuit supplying a dwelling's laundry receptacles must be rated:
- A.20 A
- B.30 A
- C.25 A
- D.15 A
Answer: A. At least one 20 A branch circuit is required for the laundry receptacle outlets, and it may not have other outlets. The dryer has its own separate circuit.
7. A 20 A circuit that supplies only bathroom receptacles may serve:
- A.Bathroom and bedroom outlets
- B.Only one bathroom's receptacles
- C.Bathroom and hallway outlets
- D.Receptacles in several bathrooms
Answer: D. A 20 A bathroom branch circuit may supply receptacles in more than one bathroom, or it may supply everything in a single bathroom. It may not pick up outlets in other rooms.
8. Along the floor line of a dwelling wall, no point may be farther than this from a receptacle:
- A.12 ft
- B.6 ft
- C.4 ft
- D.8 ft
Answer: B. Receptacles must be placed so that no point along the floor line of any wall space is more than 6 ft from a receptacle. That puts receptacles no more than 12 ft apart.
9. In the standard dwelling calculation, each small-appliance and laundry circuit is counted at:
- A.2,400 VA
- B.1,500 VA
- C.1,200 VA
- D.1,800 VA
Answer: B. Each 20 A small-appliance branch circuit and the laundry circuit are counted at 1,500 VA and added to the general lighting load before demand factors.
10. On a 20 A circuit that also supplies lighting or receptacles, fastened-in-place equipment may total no more than:
- A.8 A
- B.12 A
- C.16 A
- D.10 A
Answer: D. Fastened-in-place utilization equipment may not exceed 50 percent of the branch-circuit rating when the circuit also supplies lighting units or cord-connected equipment: 50 percent of 20 A is 10 A.